Posted 30 September 2011 - 05:17 AM

There is nothing in the code that sizes a return-air grille other than the 450 fpm that is found in section 603.18 (2012 NCMC).

I propose that a section be added to the code per the following:

"The minimum size of return-air grilles shall be 1 square inch per 2 cfm of air flow."

This gives the inspector a minimum size and the 1 SqIn per 2 cfm is the industry accepted standard to size return-air grilles.

For instance, a 2 1/2 ton AC system has approximately 1000 cfm air flow. Based on the statement above, a 500 SqIn return-air grille would be required. Any combination or number of grilles that equal or exceed the requuired size would be acceptable.


Any discussion?

#2 Paul Ezell

Paul Ezell

    President

  • Director
  • 5 posts
  • LocationShelby, NC
  • Occupation:Director

Posted 03 October 2011 - 05:46 AM

Dennis, I agree. That would make it a lot easier for inspectors in the field.
Paul Ezell